I was working with my apprentice and he asked me if all dining room receptacle circuits had to be 20 amps. He told me that someone else in the company said it was required. Since I don't do any residential work, I couldn't answer him right away.
When I looked in the 2005 NEC I found Art. 210.52(B)(1) which says:
(B) Small Appliances.
(1) Receptacle Outlets Served. In the kitchen, pantry, breakfast room, dining room, or similar area of a dwelling unit, the two or more 20-ampere small-appliance branch circuits required by 210.11(C)(1) shall serve all wall and floor receptacle outlets covered by 210.52(A), all countertop outlets covered by 210.52(C), and receptacle outlets for refrigeration equipment.
Now what I want to know is, first, am I looking at the right article and second, does this mean that all dining room receptacles have to be 20 amps?
When I looked in the 2005 NEC I found Art. 210.52(B)(1) which says:
(B) Small Appliances.
(1) Receptacle Outlets Served. In the kitchen, pantry, breakfast room, dining room, or similar area of a dwelling unit, the two or more 20-ampere small-appliance branch circuits required by 210.11(C)(1) shall serve all wall and floor receptacle outlets covered by 210.52(A), all countertop outlets covered by 210.52(C), and receptacle outlets for refrigeration equipment.
Now what I want to know is, first, am I looking at the right article and second, does this mean that all dining room receptacles have to be 20 amps?