And what about:
PANEL > LO1 > LO2 > LO3 > LO4 > NLO5
.........................|
........................R1
Where R1 is tagged off LO2, and one can say that the exisiting branch circuit HAS a receptacle outlet, but there is no way, short of additional circuit modification, for the OBC AFCI to be wired in a "feed thru" manner. Am I required, when using 210.12(B)(2), to place the OBC AFCI at R1? (NLO = New Lighting Outlet)
Why would there be no way to feed thru. I would have the afci at LO2 and feed thru to R1. In some cases you may have to go back to the panel or at LO1.
Again the intent is to protect any new wiring.