RJSteff
Member
- Location
- Rhode Island
- Occupation
- Electrician
So essentially its following 406.4 D using 212.12 location specificiationsYou're allowed to add up to 6' of a wiring method before it's considered to be a modification of the branch circuit. Having said that what I've stated is irrelevant to your question since you're only replacing a receptacle. If the replacement receptacle is in a location that requires AFCI protection then you must install an AFCI type receptacle.