210.52(5) requires a receptacle over a peninsula counter,
(5) Receptacle Outlet Location. Receptacle outlets shall be located above, but not more than 500 mm (20 in.) above, the counter top.
Would it be code compliant to use a cord drop (pendent) from the ceiling as described in 210.50 (a)
(A) Cord Pendants. A cord connector that is supplied by a permanently connected cord pendant shall be considered a receptacle outlet.
I know it would look bizarre but I had to cut in a receptacle into the side of a kitchen cabinet today and it got me thinking about how many ways you could meet code in this situation.
(5) Receptacle Outlet Location. Receptacle outlets shall be located above, but not more than 500 mm (20 in.) above, the counter top.
Would it be code compliant to use a cord drop (pendent) from the ceiling as described in 210.50 (a)
(A) Cord Pendants. A cord connector that is supplied by a permanently connected cord pendant shall be considered a receptacle outlet.
I know it would look bizarre but I had to cut in a receptacle into the side of a kitchen cabinet today and it got me thinking about how many ways you could meet code in this situation.