- Hospital Master Electrician
Might have to surface mount if installing behind the candleholder. the end of the island has a pull drawer.
It might wind up behind the sink.
A difference in elevation is not listed as an object that creates a break in counter space. It is one island, because there is plenty of counter space behind the sink to qualify.
And I respectfully disagree-- I see 2 countertops and the article specifically mentions countertops. I do not see the sink counter extending beyond the sink by 12"
Where in that section tells us a change in elevation requires another outlet?
The first few post started out stating that the rec. could be mounted in the elevation difference between the lower surface and the higher surface.
I would ask both of you if mounted flush in that vertical elevation difference between the two is the rec. mounted below or above the counter top space.
We always say when there is doubt then the benefit of the doubt favors the installer, not the strict application of the rule.
I am lost. :?
(2) Island Countertop Spaces. At least one receptacle shall
be installed at each island countertop space with a long dimension
of 600 mm (24 in.) or greater and a short dimension of
300 mm (12 in.) or greater.
No place does it say no more than one required.
Are you not the one that posted 210.52 (C) (4)?
personally, in this situation, I don't think it really matters whether 1 or 2 are required. It's obviously a custom kitchen and I'm going to sell the owner at least 2 receptacles on that island. design/convenience will dictate it.
I don't ever want an owner to spend 20, 30, 40, 50k or more and not be satisfied with my final product.
The entire piece is an island. I don't see how you can call it anything else.