If I have a room with two entrances/exits can I have a switch at one and a dimmer at the other. 210.70(A)(2)(4) says I need a dimmer at each location for 210.70(A)(2)(3) which is additional locations.
help please!
 
I worded that terribly, if I do have a switch at each entrance/exit to a room. The customer wants a dimmer in room. Do I need to add a dimmer at each entrance or can I have a dimmer at one entrance and toggle switch at the other. Where can I find in code.
 
I worded that terribly, if I do have a switch at each entrance/exit to a room. The customer wants a dimmer in room. Do I need to add a dimmer at each entrance or can I have a dimmer at one entrance and toggle switch at the other. Where can I find in code.

That is not in the code. They make switches where you can dim at both locations but it is expensive. A standard 3 way dimmer will work fine with a 3 way switch.
 
210.70(A)(2)(4) is referring to interior stairways only. If you choose to install a dimmer for the stairs, you need to be able to fully control the dimming from each of the locations required by 210.70(A)(2)(3)