That's a lot of 3Ph receptacles to need 300 in the next 3 months per OP.I believe they are being required for three phase receptacles.
That's a lot of 3Ph receptacles to need 300 in the next 3 months per OP.I believe they are being required for three phase receptacles.
Note that OP said one order was short 20 or so three pole breakers.That's a lot of 3Ph receptacles to need 300 in the next 3 months per OP.
I think the cumulative leakage is a real problem. But even if just one appliance caused a trip it will be a real issue time wise to locate. It would create havoc in a busy kitchen. Also see post 13. In my view the NEC folks and bureaucrats acting as AHJs in many cases need a reality check. People need to fight back against all these idiots.
That's a lot of 3Ph receptacles to need 300 in the next 3 months per OP.
From another thread.
-Hal
About all I can say is somebody has some fighting to do.
-Hal
The AHJ’s I do residential in are allowing temp CO’s without AFCI’s, and they were making an exception on GFCI’s for outdoor equipment; now that the state has announced they’ll amend the code to remove that requirement it doesn’t matter.
But on commercial, all have said they won’t make an exception due to liability concerns.
In commercial applications OSHA has their hands into the mix as well, where workers might be exposed to the risk.If they can do it for residential why is the liability for commercial any different?
-Hal
In commercial applications OSHA has their hands into the mix as well, where workers might be exposed to the risk.
Plus exposure is greater by the number of public individuals potentially exposed to the equipment depending of locations of the equipment. In residential the HO bears most of the liability and would be informed of the risks (informed concent), in a commercial space the process that could be viewed as informed concent would be impractical for general public access areas.
Doesn't change the risk of electrical equipment failure in either type of occupancy that could result in a shock or electrocution, just the level of exposure.