When did code start requireing a main breaker if you had more than six breakers in a panel? I was doing a fire inspection the other day and it had 5 panels in the church and only one had a main breaker. Thanks
When did code start requireing a main breaker if you had more than six breakers in a panel? I was doing a fire inspection the other day and it had 5 panels in the church and only one had a main breaker. Thanks
If these panels are in the same building, the code has never required them to have a main breaker. Article 225 does not apply within a building.When did code start requireing a main breaker if you had more than six breakers in a panel? I was doing a fire inspection the other day and it had 5 panels in the church and only one had a main breaker. Thanks