I'm rewiring a detached garage for a friend. His current setup is a 30-amp disconnect in the 200-amp primary panel for the residence protecting a 30-amp (10-3/G) cable to a Eaton CH12B 125-amp rated secondary panel in the garage.
There are 5 circuits total in the secondary panel so no need for a main disconnect in the secondary panel. My question is, shouldn't the disconnect in the primary panel be a minimum 60-amp per 225.39(D)? Which of course would dictate a 6-3/G feeder to the secondary panel.