225A fused disconnect

Status
Not open for further replies.

Rock86

Senior Member
Location
new york
Occupation
Electrical Engineer / Electrician
what size fuses are in the disconnect? I'm assuming the 225A is the rated size of the disconnect and not the fuses.
 

jap

Senior Member
Occupation
Electrician
If the disconnect doesn't fall within the tap rule, a 200a rated disconnect is not rated for 225 amps.

JAP>
 

Rock86

Senior Member
Location
new york
Occupation
Electrical Engineer / Electrician
How? 225A breaker protects 200A fused disco? Its 200A breaker is 225A???
???? Can you clarify what you have? Your numbers have changed a few times now. But either way... if the disconnect is rated for 225A but is furnished with 175A fuses, you don't have an issue.
 

kwired

Electron manager
Location
NE Nebraska
The fused disconnect protects itself. That's why it has fuses.
There is that for general applications.

For non fused switches sometimes you have horsepower rating that high enough you can end up using switch for motor disconnect where the branch circuit device is higher rating than the switch.

I've installed a lot of 60 amp non fused disconnects for 25 HP 480 volt motors though the circuit breaker supplying this is 70 amps as well as 30 amp non fused switch for 20 HP though the breaker is 60 amp.

The switch itself might be able to handle more current than the largest fuse the fuseholder can handle but switches don't really require any specific ocpd they just need to be able to handle switching the load that is connected.
 

kwired

Electron manager
Location
NE Nebraska
How? 225A breaker protects 200A fused disco? Its 200A breaker is 225A???
Have you ever seen a 200 amp tap made from a 400, 600... 1200 amp feeder?

A 200 amp fused switch or breaker would be at the end of the tap.

Same fused switch often could also be a service disconnecting means and for the most part can have no real OCPD ahead of it.
 