- Location
- Chapel Hill, NC
- Occupation
- Retired Electrical Contractor
I can feed a 200 amp panel with a 1000 amp breaker as long as the wire going to it is properly sized AND the overcurrent protective device in the panel is sized to protect the panel. So a 200 amp panel that has a 200 amp main breaker is protected because even if 1000 amp overcurrent protective device is ahead the breaker in the panel will trip before the current gets too high for the panel (or disconnect). The circuit is limited by the 200 amp (or 175 amp) fuse or breaker