So if there was a 175A breaker mounted upstream of the 200A switch you would consider it as not being protection.These may not be instantaneous fuse you know. Fuses may have Time current curves where trip is delayed. So that can see more than 175A
All UL listed switches have been tested with specific fuse types, such as Class H, R, and J which are typically time delay styles.
There is almost no general purpose protective device which operates instantaneously, in fact most overcurrent protection devices will allow 133% of current to flow for many 10s of minutes.