dnem said:
?directly,....specifically? ?
Is it just that simple, Bob ?
Who are you trying to fool by saying directly,....specifically ?
I know that you know better and I can?t believe how low you are willing to sink just to sling mud.
You used to attempt to quote the code properly.
iwire said:
David I still stand by my post, I happened to be away from my code book when I posted before but I assumed you had one and would know the rules.
Here is the code section I was thinking of.
Quote:
230.90 Exception No. 3: Two to six circuit breakers or sets of fuses shall be permitted as the overcurrent device to provide the overload protection. The sum of the ratings of the circuit breakers or fuses shall be permitted to exceed the ampacity of the service conductors, provided the calculated load does not exceed the ampacity of the service conductors.
I am not trying to fool anyone.
That section does specifically and directly allow the ratings of the OCPDs to exceed the the conductor rating.
"I assumed you had one and would know the rules"
I do know the rules and 240.4(B) is one of them.
"That section does specifically and directly allow the ratings of the OCPDs to exceed the the conductor rating."
Don't play dumb with me. You know exactly what you're saying. And you know that 230.90(A)x3 doesn't allow
unlimited load. I stated that the load calcs were
not provided and as long as the contractor sticks to Table310.15(B)(6) they
don't need to provide any. 99.9% of all our residential services go in according to Table310.15(B)(6) without any complications.
There is
no specifically and directly in 230.90(A)x3 and you know it. You've shown from past threads that you know it. But right now you're pissed at me so you're saying things that you know aren't true. You appear to say certain things only to bait a response and possibly aslo to try to score points with anyone that doesn't think thru the post completely.
dnem said:
On the original inspection there were the two 200amp breakers that were each feeding a 42 space subpanel that were both empty [the rough install was yet in the future]. In the double column push-in section of 12 KOs there was a two pole 100, a two pole 60, a two pole 40, and a two pole 30, and four KOs still not knocked out. No labeling on the panel. No contractor on site. No loads calcs or prints on residential projects in my building department. Phone number line on the permit left blank by the contractor.
So we have 200, 200, 100, 60, 40, & 30 which equals 630 amps of breakers.
The service conductors are parallel 4/0 AL.
iwire said:
You sound like a DIY when you start adding up breakers to determine the load.
Given what you describe you would be within your authority to ask for load calculations.
If they provide load calcs that are under the the conductor rating than yes this service is legal and must pass.
If they do not provide load calcs than yes I would not pass it and the citation would be 230.90 Exception 3.
The 'red tag' would not have anyting to do with lack of phone numbers, KOs not knocked out or emtpty spaces that someone may in the future break he rules with.
"You sound like a DIY when you start adding up breakers to determine the load"
When you don't have load calcs, how else would you quick check to see if there might be a problem ? If I added up all the breakers and they came to
less than 400 amps on para 4/0 AL, why would I ask for load calcs ?
Do you consider the use of
basic logic to be "DIY" ?
Every single situation doesn't require a rocket scientist to quick check whether or not to look more closely at the install.
"The 'red tag' would not have anyting to do with lack of phone numbers"
I got a suggestion on this thread that the inspection should never been performed and
that's the reason that I brought up a phone number. I can't undo the miles that I've driven to get to the jobsite. I don't get to erase the time spent driving or checking out the install/opening panels etc. When a phone number is available it can improve a situation and just maybe add enough info to change the situation from a Not Approved to an Approved.
There's no red tags for lack of phone number. But we do have reinspection fees. If one of us is called out on an inspection and it does not end with an Approval, we may have to return for another inspection for the same item. A reinspection fee would go on the contractors permit. A phone number just might bring enough info to change that outcome.
David