Existing main service switchboard is MLO has (6) main breakers (each breaker is not in a separate enclosure), we plan to replace
the main underground feeder to this switchboard with new feeder per owner's request. Can we use below exception to avoid
replacing the switchboard and code compliance?
230.71(B)
Exception to (2), (3), (4), (5), and (6): Existing service equipment, installed in compliance with previous editions of this Code that
permitted multiple service disconnecting means in a single enclosure, section, or compartment, shall be permitted to contain a
maximum of six service disconnecting means.