Yeah blame it on me for having an opinion and not trying to correct a stupid rule. What I would really like to know is what the exact proposal was that got this language into the code. I am sorry but I really don't have the time or know how to search the CMP proposals. Just a FYI here in the republic of California we are at least 3 years behind the NEC. This section came as a complete surprise.
We've always been exactly 3 years behind. Which means you had 3 years to be aware this was coming.
To get CA to make a change you need to be a Engineer. Many times stuff is just done without proper justification or vetting.
No, CA adopts the NEC (3 years behind) practically verbatim. Which means the most effective way to make a change is to involve yourself in the NEC public input process. Which does not require credentials.
Unfortunately you missed the deadline for the 2026 NEC, but there will be a round of comments, so if you see additional proposed changes to this section then you can state your support or objection for the Second Draft round.
I realize it's frustrating and demotivating that such action won't have an effect in CA until years down the road.
If someone told me that this was done to keep each customers feeder and breakers separate then maybe I'd listen. However to cause a manufacturer to design what looks like several meter mains bolted together in a row it just plain stupid. A simple divider would be all that was necessary.
For what it's worth, I completely agree with you. These changes are pretty much never substatiated with data on actual impact on injury or damage. And they often change things that weren't considered a problem for decades. But the only way to fix the process is to get involved.