Here is the story... The facility has existing 5,000A MLO switchboard (480/277, 3ph) with two main distribution breakers (2,000A and 1,200A) located in separate vertical sections. The owner requested to replace existing main service feeder to the switchboard with new feeder. The electrical inspector said the switchboard does not comply with NEC 2020 article 230.71 because the two main distribution breakers connect to same incoming main horizontal bus and they are still part of one switchboard enclosure. To comply with NEC 230.71 (B), either each swbd distribution breaker cannot share same incoming horizontal bus, or two separate switchboards must be used – i.e. each switchboard with have its own main CB and be fed from same utility transformer with separate circuit. In my opinion, this is not how code language (230.71(B)(3) says, it does not require two separate switchboards as long as each main disc. section had separate vertical barrier. Can you enlighten me? If two switchboards are used, then the building needs two separate meters even one owner???