I'm still very confused by your response, I think I am not explaining the situation correctly. I have a 230.85 emergency disconnect on the exterior of the building.
Yes, and a 230.85 Emergency Disconnect may not provide OCPD. It could be an unfused bladed disconnect. In which case the conductors going into the building would still be unfused, and the "nearest the point of entry" for the service OCPD is important.
Now if your 230.85 Emergency Disconnect does actually provide OCPD, you have two choices. You can recognize that it provides OCPD, and make it your service disconnect. Then it needs to have the MBJ, so your supply to the interior needs to be a feeder with an EGC, and you are free from the "nearest the point of entry" restriction. Any GECs/jumpers from the GES also have to go to the outside panel (unless your EGC also qualifies as a GEC).
Or you can ignore that your 230.85 Emergency Disconnect provides OCPD, and pretend it doesn't. That puts you back in the case of the first paragraph.
Basically, if you want the liberty of not running an EGC to the interior, and not moving the MBJ/GECs to the exterior, then you have to comply with the "nearest the point of entry" requirement.
This whole situation arose because the 2020 NEC wanted to require an exterior disconnect, but for ease of retrofit on existing installations, did not want to force the service disconnect itself to be outside, with the associated requirements mentioned in the second paragraph above. So you get to add this extra exterior disconnect but have the option to basically ignore it as far as the service rules go, just like you ignore the location of the meter.
Cheers, Wayne