JuliaTruchsess
Member
- Location
- Newtown, CT, USA
- Occupation
- Engineer
Say I have a load I know is going to be 278A max. After temperature and fill derating, I find that 4/0 can handle it, and 240.6(c) will let me use it with a 400A breaker if the breaker is restricted-access and "dialed-in" to 278A. But really, is it possible to get that fine an adjustment on an electronic-trip breaker with a single-turn screwdriver adjustment, especially given the inherent tolerances of trip curves? If I go to an easy-to-find spot on the dial like 300A (75%) then I have to use 250MCM. I like the logic behind 240.6(c) but it doesn't seem all that practical in real life.