JoeStillman
- West Chester, PA
- Electrical PE
Overloaded or bad harmonics. Any VFDs on the circuit?
Does this cable have a 'semiconducting' surface layer that gets grounded?
-Jon
I believe it does, but low down, behind that box.
I don't see where the cable shield is terminated and connected to ground. This should happen at the lower side of the stress cones.
Let's consider this scenario:
This being shielded cable (as Winnie inquired) and the shield connections to ground are loose/ bad and a ground fault occurred down stream then the heat from the high resistance path caused the shield to overheat and the tape discoloration. This, of course, would have to assume that the GF protective circuit did not open the breaker before the damage occurred. There are a lot of assumptions here but it warrants further investigation regarding shutting down the circuit and checking ground connections and the GF protection system. I would also find out what the history is of any faults or failures that may have occurred on this circuit thru a log book or talking with the old timers in the engineering department.
There should not be a shield between the bus terminal and the stress cone so the brown marks should not be from an overheated shield if the terminations were done correctly
delta primary
a single line fault should not allow current flow unless a shield has a path to phase
The delta primaries I mentioned earlier are only the loads on this circuit. The 13.2 kV source is grounded-wye.
I really doubt that the discoloration is from overheating, since the cable is so lightly loaded.
I think what we are seeing is corona damage to the tape. There seems to be too much unshielded cable between the cones and the termination. That and the rough surface of the tape are contributing to atmospheric ionization, resulting in nitric acid condensation in times of high humidity.
Is there a way to measure for corona?
15 kV cables operating at 13.2 kV in an outdoor main-tie-main lineup. Load is between 20 and 40 Amps.