Any grid-tie inverter just needs an external stable AC source to sync to.
The step-down PV xfmr isn't a source- if there was no service of any kind, the inverters wouldn't run.
I don't know if I'd call the grid a source- isn't it more of a...repository?
The inverters need to know the impedance of the grid.
This is sorta over my head, but I do know the grid people are the only ones who know what their codes and standards are.
The LCL filters employed in grid connected inverters are
used to pass the fundamental frequency and attenuate the rest
of undesired high order harmonics, which are appeared in the
current and voltage profiles. Although, this goal is more or
less achieved as an advantage of LCL filters, they interact with
the grid elements as a part of a resonance circuit at a point
close to the source of harmonics, i.e. inverter [13]. Harmonic
emission of inverter or the harmonics, which are coming
form the grid side may trigger existing parallel and/or series
resonance circuits. This phenomenon may magnify harmonic
level exceeding the limits recommended by grid codes and
standards leading to distorted and hence undesired waveforms
or in severe cases instability of inverter
https://arxiv.org/pdf/1612.02045.pdf
Until you ground the neutral, all four of these voltages relative to ground are undefined.
You can bond neutral to ground either in the disco on the inverter side of the transformer or at the transformer itself, but not both.
Seems like the OP described bonding it in the MSP, which would not be one or both- it'd be neither.
Nothing changes as to how the MSP is wired regardless of whether the PV system is connected supply side or load side. The service neutral must be run to the MSP. The GEC(s) for the building or structure where the service disconnect is located must connect to the service entrance conductor neutral. And a Main Bonding Jumper is required in the service disconnecting means. That's it for the MSP.
The OP described the PV neutral as ending at the PV disco, but also continuing on as a GEC thru the xfmr to the MSP.
There should be a bonding jumper in the PV disco *and* the MSP, and both ground bars (MSP/PV disco) should be connected to the GES by GECs.
That isn't how it was described.
I don't even understand how the "GEC goes thru the PV xfmr" as described...
Bus B to Bus A is 240V.
Bus B to Bus C is 240V.
Bus A to Bus C is 240V.
Bus A-N is 120V, and bus C-N is 120V.
I'm assuming that they are being used. Won't that throw off the inverter's reference somehow?
Are you sure? :lol::lol::lol::lol::lol:
PVFarmer, try this thought on for size...
Functionally, what is the difference between these two hookups?
1) ---[service point] ----3 phase system of unknown grounding and voltage ---[XFMR approved for both sides] --- 480/277V Wye --- [PV inverter designed for 480/277V Wye]
2) ----3 phase system of unknown grounding and voltage ---[XFMR approved for both sides] --- 480/277V Wye ---service point --- [PV inverter designed for 480/277V Wye]
Remember that the service point is just a legal boundary, not an electrical one. Also note that 'Grid' isn't an NEC term, and could be on either side of the service point.
Yes!
However....

The service point is what the inverter is supposed to use for grid reference, no?
One difference- in #1 the xfmr is customer owned, in #2, the xfmr is POCO owned.
In #1, the POCO's interconnection calcs are a factor which is influenced by the customer owned xfmr. Period.
1- You don't want to use a wye connection which is grounded on PV side and wye/not grounded on "grid" side if using an SMA Tripower, so a "3 phase system of unknown grounding and voltage" might work, or not.
SMA only restrictively recommends "Yyn_" transformers with a star connection on the medium-voltage side and a star
connection on the low-voltage side with a neutral point that leads outward (see figure below e.g. Yyn0)
http://files.sma.de/dl/7418/STP24-US_MV_Trafo-TI-en-10.pdf
Also, 1 doesn't make sense- how can you have a mystery service? The POCO doesn't say "here's some electricity, figure it out yourself. Good luck."
2- You don't need to know what the grid voltage is if the service and inverter are both = to 480Y/277V.
Service Point. The point of connection between the facilities
of the serving utility and the premises wiring.
Informational Note: The service point can be described as
the point of demarcation between where the serving utility
ends and the premises wiring begins. The serving utility
generally specifies the location of the service point based
on the conditions of service.
I mean, really- you can't put in an xfmr of which you don't know the voltage/grounding! I don't get this one.
??
1) ---[service point] ----3 phase system of unknown grounding and voltage ---[XFMR approved for both sides] --- 480/277V Wye --- [PV inverter designed for 480/277V Wye]