Allowed inverter shutdown time is different than fault clearing time on the transformer output time.
Then look at the trip curve of the breaker on the utility side.
Perhaps what you're not understanding is that the available fault current from the utility is at least two orders of magnitude greater than the inverter output. So for most portions of the trip curve the inverter is going to be a rounding error. The code does not require it to be addressed. By the way, this question also has nothing to do with the fact that there is a transformer in the system design. You could be asking the same thing about any inverter output connection.