mivey likes to obfuscate a simple discussion.
He cannot accept the fact that the industry does not 'universally' call 2 hot conductors and a neutral, or common, conductor 2-phase.
Jim refuses to acknowledge that 2 hot conductors and a neutral, or common, conductor is also called 2-phase by a large section of the industry.
Jim refuses to acknowledge that the naming convention he likes to promote is not a universal fit and he tries to bend the systems to fit his restrictive naming convention. I never said that the industry should universally call it by one name or another.
I do promote the idea that if people in our industry would seek to understand where the names came from by starting with a more general definition, then they would not get confused when the different naming conventions and system configurations do not match. They would also be able to see how some of the naming conventions are derived sub-sets of the general case.
Understanding where the names come from and why they apply for specific cases is not a move to drop the names we have become accustomed to.
He has written many posts promoting the practice of calling 120/240 3-wire 2-phase.
Jim is mis-representing what I have said.
The point I have tried to make in other posts is that the 3-wire 120/240 volt single-phase system maps to the same space as that occupied by a using more generalized naming conventions of poly-phase systems. Understanding generalized case helps understand why there is no conflict between the two. But that does not mean we should go re-naming everything, only that a broader understanding will show why the traditional name works for the specific case.
Just because the traditional name works for a specific case does not mean we can use the specific case to create a general naming convention. I have shown numerous times why this does not work, and actually falls apart for other specific cases.
Now in this thread, he is calling an open-wye configuration 2-phase.
Because it is common in the utility industry (my current field).
It appears mivey recognizes 2-phase systems of 90?, 180?, and 120? separation. I wonder does he call a corner grounded open-delta, 2-phase at 60?? After all it is two phase conductors with one common conductor.
If you would start listening to what I am saying, maybe you would understand and you wouldn't have to wonder because you could figure it out for yourself. The source has three, equal-magnitude, phase-displaced voltages so it would normally be labeled as a 3-phase source.
Now for how it is used:
Let the corners of the delta be a, b, and c. Let's ground a.
If the load uses the voltage Vba OR Vca, then it is a single-phase load and I am using the source as a single-phase supply.
If the load uses the voltage Vba AND Vac AND Vcb, then it is a three-phase load and I am using the source as a three-phase supply.
If the load uses the voltage Vba AND Vac (or any other combination of two equal magnitude, phase-displaced voltages), then it is a two-phase load and I am using the source as a two-phase supply.
That's right: The 3-phase source can supply all three systems.
What happens if we ground at midpoint instead? You have a combination of a three-phase configuration and a single-phase configuration that can supply 1, 2, and 3 phase loads.
I stand behind my original post
My reference materials, well at least the ones on my desk right now, (UGLY's, ANSI/IEEE C57.105, and Cooper Power Systems R201-90-2) all call the feed, to open-delta and open-wye transformer connections, as 3-phase.
By common utility language, the feed to open-delta would be 3-phase and the feed to the open-wye would be 2-phase.
And, except through the slight of hand of introducing a 3rd wire, mivey has not proven me wrong when I said:
That statement by itself is not wrong. But that was not what you asked. You wanted to know why I posted what I did. I told you why. If you don't want to listen, so be it.