I'm trying to fully understand the position of it not being a violation (like Jap and electrofelon). So to you guys, as long as it hits an OCPD within the length restriction, then it's ok?
I'm being sincere here. The word terminate, to me, means 'the connection at the end of that wire', so it's hard to agree with your "I see no such l language". And I say it's referring to the wires because it says "tap conductors terminate" and not "tap circuit terminates". But if 'terminate' doesn't have an article 100 definition, then it does seem to be a war of undefined words...
I can't speek for electrofelon, but, as far as I'm concerned, someone would have to explain to me how a tap conductor would somehow loose it's protection (not that you would but) if a splice is made in that conductor, or a switch is installed in that conductor, or being cut and wire nutted back together, or terminating line and load on a meter base, or any other item that is not an actual load as long as the tap conductor is within it's length requirements.
I simply see nothing in the language that says the tap conductor has to terminate in the overload protection terminal "first", only that it does have to terminate at an overload protection device to protect the tap conductor within a certain distance.
If the rule said that the termination at the overload protection or set of fuses had to be made "first", then, I'd understand no splice, or meter, or any other termination in the tap conductor prior to the overcurrent protection not being allowed.
JAP>