250.118 - using emt conduit as a ground

Status
Not open for further replies.

difowler1

Senior Member
Looks like it's okay in 250.118 to use emt as a ground. Is it also code to run subpanel feeder circuit without a equipment grounding conductor as long as the wires are within emt pipe the whole way?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Yes; why would think it wouldn't be?

Roger
 

packersparky

Senior Member
Location
Wisconsin
Occupation
Inspector
To add to Roger's response, many studies have shown that a metallic raceway performs better at clearing a fault than a wire type equipment grounding conductor.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
We use EMT as an EGC all of the time unless someone is paying for a wire type EGC in the raceway.
 

peter d

Senior Member
Location
New England
We use EMT as an EGC all of the time unless someone is paying for a wire type EGC in the raceway.

:thumbsup:

I don't get the obsession with wire EGC's. I always encounter EMT installations done from the 1960's to the 1980's and it never had a separate ground wire. Now it does. :roll:
 

kwired

Electron manager
Location
NE Nebraska
:thumbsup:

I don't get the obsession with wire EGC's. I always encounter EMT installations done from the 1960's to the 1980's and it never had a separate ground wire. Now it does. :roll:

Seen many from the time period you mentioned with poorly supported raceway contributing to broken fittings resulting in loss of EGC, also seen loose set screws or compression nuts, but that is all workmanship issues more than anything IMO. Have seen poorly made up EGC's in cable wiring methods as well - open continuity is still open continuity.

I do a lot of grain storage bins and handling equipment. Generally all steel structures and equipment. I do run EGC's in flexible conduits or in any non metallic raceways (which is usually just underground raceways in these applications) but see running any wire EGC in most of said systems as pointless, the equipment/structures are very effective fault return path, and usually more effective than my raceways, so if a fitting didn't get tightened it doesn't really matter much from equipment grounding perspective.
 

jap

Senior Member
Occupation
Electrician
Pulling a wire type EGC is more about a backup or assured bonding.

Much like a safety chain installed on a perfectly supported pendant fixture.

JAP>
 

jap

Senior Member
Occupation
Electrician
Plus, dropping that one conductor when emt is used, helps somewhat for the added conductors we now have to add for MWBC's that we didn't used to have to install.

That is for us old dogs that always used MWBC's and now don't like tying individual circuit handles together. :p

JAP>
 

kwired

Electron manager
Location
NE Nebraska
Pulling a wire type EGC is more about a backup or assured bonding.

Much like a safety chain installed on a perfectly supported pendant fixture.

JAP>

Which NEC only requires additional paths for certain art 517 applications (could be other specific sections but am not aware of any), outside of that it is a design decision.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Which NEC only requires additional paths for certain art 517 applications (could be other specific sections but am not aware of any), outside of that it is a design decision.

If the raceway is so good as an EGC why is there ever a need for redundant grounding? Needs to be extra good? :)
 

Besoeker3

Senior Member
Location
UK
Occupation
Retired Electrical Engineer
Haven't seen EMT used for any installations since I was doing my apprenticeship in the 1840s....and even then we had to run a separate earth (grounding) conductor... :cool:
 

480sparky

Senior Member
Location
Iowegia
Haven't seen EMT used for any installations since I was doing my apprenticeship in the 1840s....and even then we had to run a separate earth (grounding) conductor... :cool:

Man..... you're OLD!!!!!!!
phiphi.gif
 

kec

Senior Member
Location
CT
Occupation
Electrical Contractor
Seen many from the time period you mentioned with poorly supported raceway contributing to broken fittings resulting in loss of EGC, also seen loose set screws or compression nuts, but that is all workmanship issues more than anything IMO. Have seen poorly made up EGC's in cable wiring methods as well - open continuity is still open continuity.

I do a lot of grain storage bins and handling equipment. Generally all steel structures and equipment. I do run EGC's in flexible conduits or in any non metallic raceways (which is usually just underground raceways in these applications) but see running any wire EGC in most of said systems as pointless, the equipment/structures are very effective fault return path, and usually more effective than my raceways, so if a fitting didn't get tightened it doesn't really matter much from equipment grounding perspective.

Agree, if set screws are tight then your are good to go, but Ive come across installations [done by others] with duck tape used for couplings. :eek:hmy:
 