True, and I believe we're both suggesting to Zane that they need to treat their HV as service, but currently I understand he is inspecting it as a distribution feeder. Your drawing in post #18 is normal for utility service to a service disconnect.
If the system remains as a feeder the bonding jumper can be at the source and source disconnect but only through exception 2 of 250.30(A)(1): "...bonding jumper at both the source and first disconnecting means shall be permitted where doing so does not establish a parallel path for the grounded conductor", using PVC is the most common way to install this.
If the system remains as a feeder the bonding jumper can be at the source and source disconnect but only through exception 2 of 250.30(A)(1): "...bonding jumper at both the source and first disconnecting means shall be permitted where doing so does not establish a parallel path for the grounded conductor", using PVC is the most common way to install this.