How's that? (2017) 240.25(B) requires a MBJ in each service disconnecting means. I wouldn't think Exception 1 would apply to a field assembly consisting of a trough and multiple service panels.250.24 and 250.25 actually allow bonding of the neutral ahead of the disconnect so the trough could be the bonding point.
Cheers, Wayne