If the j-bolts that are in the concrete are tie wired
to the rebar is that considered bonded? Or would
you have to put in a bonding conductor wire? Could
you give a reference also. I am working on a high
school pool in Alaska. We don't build very many
pools here in alaska and the electrical engineers
are from alaska.
The EE wanted to run a 3/0 conductor
around the pool as close as possible and use that
as the bonding grid, he did not want to use the
rebar in the deck as a grid, he said the rebar grid is
an GEC and we can not use it as a bonding grid. I
wrote a RFI and straightened them and copied
article 680.26(c)(1).
to the rebar is that considered bonded? Or would
you have to put in a bonding conductor wire? Could
you give a reference also. I am working on a high
school pool in Alaska. We don't build very many
pools here in alaska and the electrical engineers
are from alaska.
The EE wanted to run a 3/0 conductor
around the pool as close as possible and use that
as the bonding grid, he did not want to use the
rebar in the deck as a grid, he said the rebar grid is
an GEC and we can not use it as a bonding grid. I
wrote a RFI and straightened them and copied
article 680.26(c)(1).