(A) Connections to Rod, Pipe, or Plate Electrodes Where the grounding electrode conductor is connected to rod, pipe, or plate electrodes as permitted in 250.52(A)(5) or (A)(6), that portion of the conductor that is the sole connection to the grounding electrode shall not be required to be larger than 6 AWG copper wire or 4 AWG aluminum wire.
roger said:True, but the issue at hand is the inspector making up his own rules or not understanding what is required by the NEC.
Now if "it's a local amendment" comes into the conversation that would be a different story but, this is in the NEC forum.
Roger
BackInTheHabit said:I've never been told if there was a local amendment. I've done what the inspectors have asked. Do what they ask, within reason, and pass your inspections. I've always had good rapport with the inspectors. In my twelve years of electrical, that is what has been required.
If you have a water pipe as an electrode it would need to be full sized to what-ever you had from 250.66 and the required "Supplimental" rods could be #6. And need only be attached to the portion of water pipe that qualifies as an electrode. If you have only rods they would need to be full-sized from 250.66. See 250.53(D)+(E)POWER_PIG said:Me again.......Roger, please forgive my ignorance, but are you saying that #6 awg is all that is required to connect the two rods?
e57 said:If you have only rods they would need to be full-sized from 250.66. See 250.53(D)+(E)
stickboy1375 said:No, actually they would be sized from 250.66 (A)![]()
Section 250.53(E) correlates with 250.52(A)(5) or (6) and 250.66(A). For example, if a metal underground water pipe or the metal frame of the building or structure is used as the grounding electrode or as part of the grounding electrode system, Table 250.66 must be used for sizing the grounding electrode conductor. The size of the grounding electrode conductor or bonding jumper for ground rod or pipe or for plate electrodes between the service equipment and the electrodes is not required to be larger than 6 AWG copper or 4 AWG aluminum.
e57 said:Depending on where you start - you end up in the same place with the same sized conductor through exceptions or other requirements. A full sized water and/or steel, a #4 UFER and #6 to rods and plates etc. Unless they are the sole conductor to sole electrodes then 250.66.
250.53(E), and 250.66(A) roughly say the same thing different ways.:roll:
Commentary from 250.53E:
e57 said:If you have only rods they would need to be full-sized from 250.66. See 250.53(D)+(E)
No I guess I'm either not writing it right or you're mis-understanding me - probably me not writing it right.....stickboy1375 said:Correct me if I'm wrong, but your post are saying If i'm only using rods I need to use table 250.66?
roger said:What ever makes you happy.
Roger
BackInTheHabit said:We are required to use two (2) 8' ground rods 8' apart on a 200 amp service. Whether this is new construction or a service upgrade.
And yes. It is new construction as I was originally referring to.
Grading contractors do work other than new construction.
I'm not the grading contractor but the electrical contractor.
POWER_PIG said:Call me thick headed, but I cannot wrap my fat head around this concept.
If you utilize an underground metalic water pipe for your GEC connection it has to be sized in accordance with 250.66....right?.
Additional connections would be considered a bonding jumper 6awg max....right?
your saying that 2 rods only would fall under the 250.66a?
POWER_PIG said:Ok, but if all you have, say at a residence is the two ground rods then the conductor from the service down to the first rod is to be sized from 250.66? or no?...........
POWER_PIG said:your saying that 2 rods only would fall under the 250.66a? I can clearly read thats whats its saying, but it seems to get a bit tricky when ya toss 250.66 in the mix.
POWER_PIG said:Now I understand, Thanks to all for your time. I know of some local inspectors that may need to join this forum and get reaquainted with NEC for what it says, not what they think it says. LOL
infinity said:My point was that for new construction you should be be using a CEE and no rods at all. That is unless there is not rebar in the footing.