jxofaltrds
Retired ESI
- Mike P. Columbus Ohio
- Creator
I have been told that my thoughts on 250.6 are unique. So I would like to hear how others read (A) & (B) below.
When does 250.6 apply? Sounds like some say never.
(A) Arrangement to Prevent Objectionable Current. The grounding of electrical systems, circuit conductors, surge arresters, surge-protective devices, and conductive normally non? current-carrying metal parts of equipment shall be installed and arranged in a manner that will prevent objectionable current.
(B) Alterations to Stop Objectionable Current. If the use of multiple grounding connections results in objectionable current, one or more of the following alterations shall be permitted to be made, provided that the requirements of 250.4(A)(5) or (B) (4) are met:
(1) Discontinue one or more but not all of such grounding connections.
(2) Change the locations of the grounding connections.
(3) Interrupt the continuity of the conductor or conductive path causing the objectionable current.
(4) Take other suitable remedial and approved action.