Have you actually run the numbers? It should clear it up for you.you may find it easier if you draw it out
Have you actually run the numbers? It should clear it up for you.you may find it easier if you draw it out
100% absolutely not.
If you take the load current as I then the current in the corresponding phase line is also I, and the voltage drop is IR where R is the one way resistance of that conductor.
There is no place that you can logically shoehorn in the 1.73 no matter how hard you try.
The reason that the 1.73 shows up for delta (line to line load) calculations is that the load current is NOT equal to the line current when the loads are balanced. Or at least that is one way of looking at it.
Have you actually run the numbers? It should clear it up for you.
Run 2 wires line-N out of a 120/208 panel to a load
calculate the V drop based on 1 way length
then measure it
do that for each phase with a balanced load
I was very clear at the start that I was referring to a "full boat" (three out of three phases) MWBC for the three phase. The two out of three 120/208 panel does not meet those conditions.
And, FWIW, if you have two line to neutral loads in such a panel, connected to opposite phases, each drawing current I, then the current in the neutral is also I, not 2I or 1.73I or 1.73I/2. But I am not counting that as "balanced".
And, again in the case you propose, which I did not intend to consider, the voltage drop seen by the load will (first guess, not 100% confirmed) be 1.73IR rather than 2IR since the phase VD and the neutral VD are not in phase.
Not quite. You do not get to define my assertion, I do.The assertion was that for a line-n load off a balanced 3 phase source only 1 way distance need be considered
I have not put pencil to paper. Started to but as soon as you actually think about it the results you will get are clear so I did not need to actually write it out.obviously you have not
Not quite. You do not get to define my assertion, I do.
My assertion was that for a balanced set of line-n loads (i.e. three loads) off a three phase source only one way distance need be considered.
Elsewhere (earlier) in the discussion I stated the basic condition that for a single, unbalanced, isolated, line to neutral load (whether single sided 120, 120/240 or 208Y/120), the two way distance should be used.
I have not put pencil to paper. Started to but as soon as you actually think about it the results you will get are clear so I did not need to actually write it out.
I just thought it would help you. If I get froggy I'll run TD analysis and share the results. Maybe that will clear it up for you.
Of course. That has been covered. But is not what GoldDigger was talking about in part #2.a remote line to neut load sourced from a balanced wye needs both line Z factored into the V drop calc between source-load
Of course. That has been covered. But is not what GoldDigger was talking about in part #2.
If you mean he was talking about only one single-phase load on a three-phase source, you are mistaken. Go back and read it again. He actually made the point more than once in the same post. I did not read it carefully the first time either.sure it was
Then why did you argue against it? GoldDigger made the point about balanced loads and using the one-way (line Z) and no return (neither N nor the other two lines) to find the L-N drop.it goes without saying (so no idea why it was brought up)
wye to wye 4W balanced
convert to 1 ph equiv
line will have line Z
neut 0 Z since no i flow, hence no v drop
a mental but pointless exercise
Of course. And that has been stated already. The OP had one single-phase load, not a set of balanced loads across three phases.when calculating v drop for the real world it is calculated across ph-ph, so 2 line Z are needed
If you mean he was talking about only one single-phase load on a three-phase source, you are mistaken. Go back and read it again. He actually made the point more than once in the same post. I did not read it carefully the first time either.
Someone mentioned pulling a single phase load from a balanced source (balanced source normally meaning voltages are balanced). GoldDigger was talking about a balanced set of L-N loads across a three phase source.
If you are still saying you need two line Zs (out & back) or something other than one line Z to calculate the volt drop on one of the three L-N balanced loads, you are still wrong.
Then why did you argue against it? GoldDigger made the point about balanced loads and using the one-way (line Z) and no return (neither N nor the other two lines) to find the L-N drop.
Of course. And that has been stated already. The OP had one single-phase load, not a set of balanced loads across three phases.
Hoorah! Hoorah! You are preaching to the choir brother! That point is not in dispute.You still don't get it
3 ph 4W panel
balanced
circuit pulled to remote load, 2W
both line Z must be considered MUST
Yes, yes, yes, we all know what the OP talked about and we discussed that as well. The later discussion was about your insistence that the L-N voltage drop on a set of balanced L-N loads on a three-phase MWBC required a two-way calc.read the OP
no mention of wye-wye 4W with balanced l-n loads and V drop across the neutral
Zippo
Nadda
Zilch
Hoorah! Hoorah! You are preaching to the choir brother! That point is not in dispute.
What you disputed was that the L-N voltage drop on three balance L-N loads on a three-phase MWBC only required a one-way calc. I don't know why this is a problem for you.
Yes, yes, yes, we all know what the OP talked about and we discussed that as well. The later discussion was about your insistence that the L-N voltage drop on a set of balanced L-N loads on a three-phase MWBC required a two-way calc.
Previously posted....it goes without saying (so no idea why it was brought up)
wye to wye 4W balanced
convert to 1 ph equiv
line will have line Z
neut 0 Z since no i flow, hence no v drop
a mental but pointless excercise.....
FYI, posts are available for all to review so there is no value in you trying to re-write history.In my previous post
1 ph equivilent ckt
Z in supply
no Z in return
0 idea why this was brought up
read the OP
A mwbc was never a topic, until I made the example of a remote load (which is the point of THIS thread)
when the he k will you use this knowledge?
lol
I am a little flustered because the size of wire I'm coming up with for my load seems ridiculous.
21.7 Amp total load
120 volt single phase
1317 foot run
PVC conduit
3.09 Voltage drop
I come with 250MCM!!? I never had a run that long but thats that just doesn't seem right.... All I am powering is two arm gates and a little control equipment. The engineer somehow came up with 58 amps (I don't know how) and has me running parallel 250MCM!
Am I going crazy or are the calculations correct?
Thanks for your time!
Are you saying a voltage regulator is for regulating voltageA voltage regulator at the load end may be more economical than two transformers and it offers better voltage regulation also.