You are trying to think in the right direction, but I think that you missed.Although on a balanced 3 ph system the 3 line i's mathematically cancel at the neutral and no i flows to the X0 (zero seq reactance) that does not mean a loads i evaporates
the sum is 0 but each current has value, a composite of other ph loads
if balanced ia + ib = -ic and so on
it returns on a different phase so a V drop results
total roundtrip length must be consider
with ph considered sqrt3 vs 2
I still use 2 lol
If the voltage is zero, whether it is the result of no current or three currents that add up to zero the effect on load current and power loss will be exactly the same.
If you are looking at a single load which will be operated independently and may be the only load on that three phase branch (whether single phase or part of an MWBC) I agree that you are justified in doing the two wire calculation.