He needs 22 A at 120
only 4.4 at 600 or 5.5 at 480
480 use 10 cu or 8 al
600 12 cu or 10 al
all single phase
run it with these numbers
all should be < 5% drop
No conduit
direct burial uf
Correct. Sleeving is technically not code compliant. I'm ok with violating that one.
You always pull all conductors out of all raceways if changing say a panelboard/cabinet so that you are in compliance with that section in those type of instances?Is that compliant with 300.18(A)? (2008 NEC)
You always pull all conductors out of all raceways if changing say a panelboard/cabinet so that you are in compliance with that section in those type of instances?
Correct. Sleeving is technically not code compliant. I'm ok with violating that one.
Yeah, especially if:
the raceway would be one long sleeve and not really capable of having more conductors pulled thru it in the future. That said, a quarter mile db is a long way to have the chance of improper backfill ruining the cables. The customer is already ok with raceway costs, might as well run a proper one. Maybe even a chance to upsell other receptacles/lighting along the way. 2 or 3 pullboxes would make pulling cable a piece of cake.
My utility has many 50A loads at 240/120 that are often 1000+ feet from the the main load centers. The utility uses two pole 480V breakers to run two legs to a 480 to 240/120 dry type transformer at the load. These transformers usually can accept 480 or 240 input so they can also be used at locations without 480V. Sizes of the transformers range from 5kVA to 12kVA depending on the load. Often it's 45A of staggered start motors, 60W lights, 300W heaters, and a 15A convenience outlet.
He needs 22 A at 120
only 4.4 at 600 or 5.5 at 480
480 use 10 cu or 8 al
600 12 cu or 10 al
all single phase
run it with these numbers
all should be < 5% drop
No conduit
direct burial uf
UF is 600 v rated
you can also get UL listed splice kits
try to route it to avoid areas where water may lie
plow it in
Butt splices and heat shrink if you have to splice it and do not want to consider Cable con.
Genearally you can get a pretty good price on larger spools of wire. They will custom cut to length with all of the conductors on one spool. Saves a lot of labor for the bigger stuff. Maybe not for #6.
Do do not skimp on conduit size if you end up pulling it in. Not a good choice
I went to the cable con website and did't see anything there that would match my needs. Everything on there site seemed to be for communication/data. If I'm missing something please fill me in.
Thanks!
Are you referring to a splice kit with no J-box? I'm searching now...
Found them. They only go to #8 from what I have found so far. The engineer still wants to plan on future use so he has calculated 6100va so I'll need a splice kit for #6 at 480v.
www.paigeelectric.comI went to the cable con website and did't see anything there that would match my needs. Everything on there site seemed to be for communication/data. If I'm missing something please fill me in.