domelectric
- Sarasota, Florida
What if I used one 12-3 for the two SA circuits, one 12-3 for the microwave and refrigerator, and one 12-3 for the D and D? Any input. You guys are great!
necnotevenclose said:So to correct my self I do think you can do that, but at a risk that while running the microwave the refrigerator may start to cycle which may cause the wire to overheat and or the breaker may trip.
iwire said:NEC...
iwire said:As the OP said 12/3 not 12/2 I think we can assume there will be a 20 amp breaker suppling each.
I'm just skeptical on circuiting microwaves and refrigerators to the same circuit. I wouldn't want my breaker that feeds my microwave taking out my refrigerator
Aren't the potential consequences (no pun intended) of loosing the utility neutral the same; whether-or-not the branch circuit is MW?Dennis Alwon said:The use of a multiwire circuit can be penny wise but may be pound foolish. If the utility loses a neutral ...
That is correct. I guess losing the utility will affect either situation.NoVA Comms Power said:Aren't the potential consequences (no pun intended) of loosing the utility neutral the same; whether-or-not the branch circuit is MW?
Dennis Alwon said:I guess losing the utility will affect either situation.
I don't recall having much of a problem with that, myself - but I would also route my homerun around to the bottom of the panel if necessary.Lawnguy said:In many instances, like 200a 40-ckt panels, the prospect of installing up to 40 2-wire cables is frightening.
georgestolz said:In residential, in terms of box fill, I found very few occasions where I found MWBCs handy. I used single gangs with 21 cu. in. of space - I don't see how 12/3 could be used for countertop GFIs, unless the 12/3 is looped from box to box, and the phases are used alternately, tying the other phase through for the next box.
georgestolz said:There was a guy at our shop who'd go out of his way to pull MWBCs, and consistently had a problem with box fill. If I kept it simple I didn't have to think about box fill, so instead of standing and thinking I could be pulling the next home run.
danickstr said:i thought bi-wired had to have a bar in the two breakers