Hello all - we teach this in our safety training classes. OSHA 1910.333 requires unqualified persons remain at least 10' from energized lines operating >600V. OSHA 1910.269 is written for qualified workers and permits closer approaches (as does 1926 Subpart K). In this accident, 6" was mentioned - so they were closer than ANY of the distances that OSHA has permitted since 2014! I know that this is old, but here is the link to the actual tables: https://e-hazard.com/osha-faqs-for-29-cfr-1910-269-and-29-cfr-part-1926-subpart-v/
I attended a lecture at the IEEE Electrical Safety Workshop (https://electricalsafetyworkshop.com/) around 2020 that presented BLS data showing that the largest number of electrical fatalities at high voltage are unqualified persons making contact with powerlines. We are trying to get the safety message out there, but it is so difficult to reach this target audience of residential contractors, tree trimmers, home DIYs....we are writing blogs, publishing articles, attending NEC and NFPA 70E meetings etc...still a long ways to go!
I attended a lecture at the IEEE Electrical Safety Workshop (https://electricalsafetyworkshop.com/) around 2020 that presented BLS data showing that the largest number of electrical fatalities at high voltage are unqualified persons making contact with powerlines. We are trying to get the safety message out there, but it is so difficult to reach this target audience of residential contractors, tree trimmers, home DIYs....we are writing blogs, publishing articles, attending NEC and NFPA 70E meetings etc...still a long ways to go!