Tpiekarczyk
New User
- San Dieog, CA
I would love to see an inspector insisting on support for a close nipple joining two adjacent boxes.Until such time as the NEC has a rule that says the conduit termination is permitted to serve as a conduit support, it is my opinion that all conduits and nipples, no matter how short, require a support.
So they can add it again in the next code cycle. Heck, they are running out of ideas. :lol:For a code cycle you were allowed to have up to 18" nipples without support. Why they went back to the original rule that requires a support even for the nipple installation shown in the photo is beyond me. :slaphead:
With realization that the IAEI "NEC 11 Analysis of Changes" is an opinion, it appears to me (another opinion) that they are saying the change from '08 to '11 where ***(C) was omitted, allows 3 ft of unsupported conduit between terminations.
I don't see how the code wording that says a conduit must be supported with 3' of a box, can be read as saying unsupported conduits up to 3' are permitted.With realization that the IAEI "NEC 11 Analysis of Changes" is an opinion, it appears to me (another opinion) that they are saying the change from '08 to '11 where ***(C) was omitted, allows 3 ft of unsupported conduit between terminations.
344.30(C) Unsupported Raceways. Where oversized, concentric
or eccentric knockouts are not encountered, Type RMC
shall be permitted to be unsupported where the raceway is
not more than 450 mm (18 in.) and remains in unbroken
lengths (without coupling). Such raceways shall terminate
in an outlet box, junction box, device box, cabinet, or other
termination at each end of the raceway.
I wonder why they used sealing locknuts on a 4s box
The 2008 had this as a code change:
The 2011 deleted 344.30(C).
The intent of Ryans proposal was to get the interpretation of the rule. Strapping a 1/2" 12" long makes sense, what about a 3" dia x 12" long?