From ROP:
8-35 Log #2201 NEC-P08 Final Action: Accept
(344.30(C))
_______________________________________________________________
Submitter: James W. Carpenter, International Association of Electrical
Inspectors
Recommendation: Delete this provision. Also, delete the clause “or permitted
to be unsupported in accordance with 344.30(C)” from the last sentence of
344.30.
Substantiation: The concept of a special support rule for short lengths of
raceway run between enclosures of various sorts was added to the 2008 NEC
for the first time in the history of the NEC with negligible technical
substantiation and no evidence of loss experience, and remains at variance
from routine trade practice. The existence of a coupling now immediately
provokes a support requirement, even on a 6-inch and a 4-inch long heavy-wall
4 trade size steel nipples put together to make an 11-inch (approx.) combined
raceway. A 90 degree sweep roughly 2 trade size or larger (any centerline
length over 18 in.) now requires intermediate support. The literal text now
requires support to structure on a 3-in. nipple if even one of its ends
“encounters” a concentric knockout.
Although there are those who believe the new rule simply offers limited
relief from a rule that required all raceways to be independently supported,
routine field experience throughout the history of rigid raceway wiring methods
does not substantiate such assertions. We are unaware of any significant
attempts to require supports on short nipples. All rigid raceways under NEC
rules must be listed, including their couplings; is it conceivable that a coupling
between two segments of a short (3 ft or less) nipple so seriously degrades the
stability of the raceway that such a support is needed? Concentric knockouts in
enclosures are reviewed as part of the UL 50 process, and as anyone working
these enclosures recently should be aware, those standards have been
strengthened and these knockouts are now more robust than in previous
decades; is this the time to require even more support?
Raceways generally require support within 3 ft of terminations, and when the
entire length is just that long or shorter, no additional support should be
needed. In effect, the locknuts and bushings or connectors and locknuts at each
end are supports. This is not a new concept for the NEC: CMP 7 just added the
wording “(wiring method) fittings shall be permitted as a means of cable
support” in a number of cable articles. If carried to its logical conclusion and
routinely enforced (however unlikely), this new support rule will likely drive
the market in the direction of cabled wiring methods without any technical
justification.
It should be remembered that supports to structure are not infallible. Many
raceways hang from threaded rod of indefinite length every 10 ft or so and
within 3 ft (5 ft. in some cases) of enclosures, depending on the specific rules
for the size and character of the supported raceway. Such support clearly meets
the rules in this section, but would it add anything to a nipple between
enclosures? Further, even when rigid supports such as one-hole clips are used,
the raceway beyond the last clip can have an indefinite number of couplings
and enter the center knockout of an indefinite number of concentric knockouts;
how is this arrangement so inherently more secure than a nipple between
enclosures? This new NEC provision was without precedent, and addressed a
nonexistent problem.
Panel Meeting Action: Accept
Panel Statement: CMP-8 does not necessarily agree with the submitter’s
substantiation. Securement requirements are found in 344.30(A).
Number Eligible to Vote: 12
Ballot Results: Affirmative: 11 Negative: 1
Explanation of Negative:
GRIFFITH, M.: See my explanation of negative vote on Proposal 8-24a.
Comment on Affirmative:
DABE, J.: See my statement for 8-24(a).
Also, rejected:
8-36 Log #3068 NEC-P08 Final Action: Reject
(344.30(C))
_______________________________________________________________
Submitter: Mike Holt, Leesburg, FL
Recommendation: Revise text as follows:
(C) Unsupported Raceways. Where oversized, concentric or eccentric
knockouts are not encountered, Type RMC shall be permitted to be
unsupported where the raceway is not more than 450 mm (18 in.) and remains
in unbroken lengths (without coupling). Such raceways shall terminate in an
outlet box, junction box, device box, cabinet, or other termination at each end
of the raceway.
Substantiation: This requirement is overly restrictive.
Panel Meeting Action: Reject
Panel Statement: See panel action on Proposal 8-35.
Number Eligible to Vote: 12
Ballot Results: Affirmative: 12
8-35 Log #2201 NEC-P08 Final Action: Accept
(344.30(C))
_______________________________________________________________
Submitter: James W. Carpenter, International Association of Electrical
Inspectors
Recommendation: Delete this provision. Also, delete the clause “or permitted
to be unsupported in accordance with 344.30(C)” from the last sentence of
344.30.
Substantiation: The concept of a special support rule for short lengths of
raceway run between enclosures of various sorts was added to the 2008 NEC
for the first time in the history of the NEC with negligible technical
substantiation and no evidence of loss experience, and remains at variance
from routine trade practice. The existence of a coupling now immediately
provokes a support requirement, even on a 6-inch and a 4-inch long heavy-wall
4 trade size steel nipples put together to make an 11-inch (approx.) combined
raceway. A 90 degree sweep roughly 2 trade size or larger (any centerline
length over 18 in.) now requires intermediate support. The literal text now
requires support to structure on a 3-in. nipple if even one of its ends
“encounters” a concentric knockout.
Although there are those who believe the new rule simply offers limited
relief from a rule that required all raceways to be independently supported,
routine field experience throughout the history of rigid raceway wiring methods
does not substantiate such assertions. We are unaware of any significant
attempts to require supports on short nipples. All rigid raceways under NEC
rules must be listed, including their couplings; is it conceivable that a coupling
between two segments of a short (3 ft or less) nipple so seriously degrades the
stability of the raceway that such a support is needed? Concentric knockouts in
enclosures are reviewed as part of the UL 50 process, and as anyone working
these enclosures recently should be aware, those standards have been
strengthened and these knockouts are now more robust than in previous
decades; is this the time to require even more support?
Raceways generally require support within 3 ft of terminations, and when the
entire length is just that long or shorter, no additional support should be
needed. In effect, the locknuts and bushings or connectors and locknuts at each
end are supports. This is not a new concept for the NEC: CMP 7 just added the
wording “(wiring method) fittings shall be permitted as a means of cable
support” in a number of cable articles. If carried to its logical conclusion and
routinely enforced (however unlikely), this new support rule will likely drive
the market in the direction of cabled wiring methods without any technical
justification.
It should be remembered that supports to structure are not infallible. Many
raceways hang from threaded rod of indefinite length every 10 ft or so and
within 3 ft (5 ft. in some cases) of enclosures, depending on the specific rules
for the size and character of the supported raceway. Such support clearly meets
the rules in this section, but would it add anything to a nipple between
enclosures? Further, even when rigid supports such as one-hole clips are used,
the raceway beyond the last clip can have an indefinite number of couplings
and enter the center knockout of an indefinite number of concentric knockouts;
how is this arrangement so inherently more secure than a nipple between
enclosures? This new NEC provision was without precedent, and addressed a
nonexistent problem.
Panel Meeting Action: Accept
Panel Statement: CMP-8 does not necessarily agree with the submitter’s
substantiation. Securement requirements are found in 344.30(A).
Number Eligible to Vote: 12
Ballot Results: Affirmative: 11 Negative: 1
Explanation of Negative:
GRIFFITH, M.: See my explanation of negative vote on Proposal 8-24a.
Comment on Affirmative:
DABE, J.: See my statement for 8-24(a).
Also, rejected:
8-36 Log #3068 NEC-P08 Final Action: Reject
(344.30(C))
_______________________________________________________________
Submitter: Mike Holt, Leesburg, FL
Recommendation: Revise text as follows:
(C) Unsupported Raceways. Where oversized, concentric or eccentric
knockouts are not encountered, Type RMC shall be permitted to be
unsupported where the raceway is not more than 450 mm (18 in.) and remains
in unbroken lengths (without coupling). Such raceways shall terminate in an
outlet box, junction box, device box, cabinet, or other termination at each end
of the raceway.
Substantiation: This requirement is overly restrictive.
Panel Meeting Action: Reject
Panel Statement: See panel action on Proposal 8-35.
Number Eligible to Vote: 12
Ballot Results: Affirmative: 12