From those measurements, the ONLY possibility is that you have a 240/120V 3 phase 4 wire delta source with a center tapped leg between two of the phases. That is not “Wye” at all and if they were referring to the primary side of the transformer being Wye, that was irrelevant and superfluous information that only confuses things.
So the ONLY two issues you have with this system are that 1) you can only feed 120V loads from two of the phases, and 2) if you feed 240V single phase loads where either pole comes from the “stinger” leg, the breaker cannot have a “slash rating”, meaning it must be rated for straight 240V, not “120/240V” as the cheaper ones are. Other than those two issues, you can use this in any way you need. No need to change anything.
If you have loads that need 208V phase to neutral, technically yes. The problem with doing that is that it is "unconventional", meaning that it is not what one would EXPECT to see, so the NEXT GUY to look at it may not fully understand the cobbled up arrangement and it can lead to errors that could be dangerous. I try to stay away from unconventional arrangements for that reason.If using a 277/480 panelboard with a system like this (because few if any 240V straight rated single pole breakers exist), can you connect 1-pole circuits to the high leg, and use them to feed 208V loads?
189707-2430 EDT
markebenson:
Those measurements tell you that you have a wild leg delta. If there are two transformers, then it is an open delta. Three transformers and it is a closed delta. Between two legs of the supply you have a center tapped secondary with the center tap being nreutral. This neutral should be earthed some where.
.
Well the Pike guys told you wrong.
Roger
From those measurements, the ONLY possibility is that you have a 240/120V 3 phase 4 wire delta source with a center tapped leg between two of the phases. That is not “Wye” at all and if they were referring to the primary side of the transformer being Wye, that was irrelevant and superfluous information that only confuses things.
So the ONLY two issues you have with this system are that 1) you can only feed 120V loads from two of the phases, and 2) if you feed 240V single phase loads where either pole comes from the “stinger” leg, the breaker cannot have a “slash rating”, meaning it must be rated for straight 240V, not “120/240V” as the cheaper ones are. Other than those two issues, you can use this in any way you need. No need to change anything.
The #1 RULE positively identify what you are working before you do anything .
Unfortunately the venue will use 208/240 only for 1 air conditioner and one water heater and all other devices required 110/120v and there is a new 3 phase panel for this load.
You could if you put a 208V to 120V transformer phase to neutral on the high leg, but then of course your B phase to A and C phase voltages will be 138.5V. instead of 240V. I am not recommending it, of course.There is no way to power 120 volt loads on all three phases of a high leg delta service.
But why not? Other than that the high leg may be already fully loaded, what harm could you do as long as you fed a 208V load with it?I've always heard that you should not attempt to power anything from the high leg to the neutral, period.
But why not? Other than that the high leg may be already fully loaded, what harm could you do as long as you fed a 208V load with it?
But why not? Other than that the high leg may be already fully loaded, what harm could you do as long as you fed a 208V load with it?
Pre coffee remark redacted
The slash rating of the breaker would be violated. Unless you are using a fused disconnect or a 277/480V panelboard to connect it, you are limited to 120V phase to ground nominal.
But why not? Other than that the high leg may be already fully loaded, what harm could you do as long as you fed a 208V load with it?
I have heard the voltage regulation is poor. I Dont remember if that is only if its open delta, or its BS irregardless (not a word).
But the way OP, can we be nice to the high leg? We can't control what hand we were given. How would you like to be called a bastard?