OK...question....with a nameplate motor speed of over 3400 RPM, how could someone possibly see rotation direction visually? Just curious.......In your case, I would have guessed the load was driving the motor backwards due to backflow when the motor was off.
Also a comment....(of course)....When "bumping for rotation" I have always changed rotation in the pecker head, not at the starter. Starter load side was always ABC CW (that's also the way our utility wired services and substations) left to right when testing with a phase rotation tester. I also wrote the color connections on the inside of the pecker head cover. That way, you can always keep the color codes for motor loads the same at the MCC. Eliminates possible confusion if you disconnect the motor leads at the starter and you (after a rough weekend) or the guy on the next shift aren't sure how they were connected. Troubleshooting motor controls usually involves disconnecting the motor leads to prevent starting the motor. Many pumps can suffer severe damage if they are run in reverse, even for a short time. Mechanical seals, ratchet anti-backflow, etc. I guess it was my Navy and nuclear training. I taught all of the guys "under me" to do it that way as well. OK...another sermon over with! Happy New Year:dunce: