I’m betting the installer is saying to pull power off the same feed as the bailer. I take it the tilter handles the bales? If so, both would not be running at the same time would be his logic.
 
The mfr said 7.8 amps at 208v. How would I tap off a 60 amp compactor switch box to a 7.8 amp tilter ? Wouldn't the 60 amp 3 phase breaker allow too much power to the new tilter ? Thank you for your help.
 
The mfr said 7.8 amps at 208v. How would I tap off a 60 amp compactor switch box to a 7.8 amp tilter ? Wouldn't the 60 amp 3 phase breaker allow too much power to the new tilter ? Thank you for your help.
The new machine should/might have a disconnect fused at what the machine requires. If it doesn't, then add a disconnect and fuse it to the size needed.
 