Not open for further replies.

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
I’m betting the installer is saying to pull power off the same feed as the bailer. I take it the tilter handles the bales? If so, both would not be running at the same time would be his logic.
 

Stevenfyeager

Senior Member
Location
United States, Indiana
Occupation
electrical contractor
The mfr said 7.8 amps at 208v. How would I tap off a 60 amp compactor switch box to a 7.8 amp tilter ? Wouldn't the 60 amp 3 phase breaker allow too much power to the new tilter ? Thank you for your help.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
The mfr said 7.8 amps at 208v. How would I tap off a 60 amp compactor switch box to a 7.8 amp tilter ? Wouldn't the 60 amp 3 phase breaker allow too much power to the new tilter ? Thank you for your help.
The new machine should/might have a disconnect fused at what the machine requires. If it doesn't, then add a disconnect and fuse it to the size needed.
 