If i am using a 3 phase delta wye transformer to feed a 120/208v single phase panel, is there any code that states i still have to take all 3 phases to the transformer or can i just feed it with a 2 pole breaker?
Primary yes. Need it there to work.
LarryFine said:All of which would lead to "Why have a 3-phase transformer?"
The issue is that 120/208 sinle phase is not true single phase. Call it psuedo-single-phase perhaps... since there is still a phase relationship for line1-to-neutral-to-line2. Using a delta-wye configured transformer to derive the 120/208 requires all three phases to be present on the primary. If the design permits, the unused windings should be disconnected and shorted end-to-end.If he only wants single phase on the secondary then he will only need single phase on the primary.
I'm thinking the same thing. OP, are you just trying to use what you have available or is there some other reason you are asking this question?
A three-phase transformer is just three single-phase transformers inside the same box. If you don't want to use all three of them, the others will still work fine. The worst thing I could say about it would be that it is wasteful. If you're OK with that, go for it.
Many dry-type transformers, especially those that have voltage taps on the primary, would permit one winding to be disconnected and shorted....You would have to have two secondary windings, and I don't see how you can connect just two delta primary windings on a 3-phase transformer.
It'll work when fed and connected properly.I don't think what you're proposing will work.
TTBOMK, 120/208V 1? 3W is a standard IEEE voltage.As far as the Code issue - the fact that it is not a 'standard' voltage (as defined by IEEE) may have some bearing.
TTBOMK, 120/208V 1? 3W is a standard IEEE voltage.
Don't know what TTBOMK means...
TTBOMK = to the best of my knowledge.
Yes, but that manifests itself by producing only 208v line-to-line, which IS single phase. Granted, that is offest slightly time-wise from the rest of the system, but that doesn't matter; only the voltage does.The issue is that 120/208 sinle phase is not true single phase. Call it psuedo-single-phase perhaps... since there is still a phase relationship for line1-to-neutral-to-line2.
I have, in an apartment building. Each tenant receives 120/208 1ph. It looks and works just like your home's service, with the exception that line-to-line loads receive only 208v.I also don't think I've ever seen a 208/120 single phase panelboard.
... Each tenant receives 120/208 1ph.
Correctamundo.They are all fed from a 3-phase 208Y/120v service, right?
It certainly may be.(Does the panelboard namplate say 120/208 1-phase?)
It happens all the time.No problem - 2-pole breakers in a 3-phase panelboard.
(Does the panelboard namplate say 120/208 1-phase?)
Do you though?You talking Primary or Secondary?
Primary yes. Need it there to work.
the secondary wye (star) winding in phase with that will produce its rated voltage.