Hello,
I have installed a 45 kVA 480V 3ph / 240V 3ph w/120V CT. This particular transformer was installed, not for the need of 240V 3ph, but for 120V 1ph. The reason I went with a 3ph transformer was to keep an equal load on all 3 legs of our 3ph 4 wire system (I was told to do this by my boss at that time). Needless to say I now have a new boss that trusts my knowledge in installing what is appropriate. However, I have come to a point where I am needing to install another transformer that is identical to the first one I explained (I already have it on location).
So, here's my questions...
In reading the specs for this 45 kVA transformer, it gives these... "Installation Notes. CAUTION: When using the 120V center tap for single-phase applacations, the single-phase load should not exceed 5% of the three-phase kVA rating. Connect the X3 "high leg" tot he "B" phase per NEC 384-3 (do not use X3 leg for 120V lighting)."
This has caused 3 questions for me.
1. I did not know this, and I've already installed 1 of these solely for the 240/120 1ph. I connected all 3 legs on the primary side and only X1, X2, and X4(center tap). X3 was left unterminated. This particular transformer is supplying 4 - 20A 120V circuits, each of which rarely(if at all) will pull 20A and a drill press which operates on 240V at approx. 9.5A. So, am I OK in this setup? Hopefully so, because to explain that I need to change all that equipment out will go over like a lead balloon.
2. I have an indentical transformer as the one described above (just got it delivered yesterday). My plan was to wire it the same way. It will be supplying 6 - 120V 20A circuits, again each of which will never pull the full 20A. I'd be surprised if this system pulls 20A total across all circuits combined. Am I OK to continue with this plan? OR should I redesign and start over? I think I'll be OK, but would like to know what you more experienced folks think.
3. I will be installing another system like the ones described above, only a tad bit bigger. The plan was to use a 75 kVA transformer (same configuration as previous transformers). However, this system was to supply 3 welders and a plasma cutter (4 - 50A circuits), and several 120V circuits for grinders and sanders. These circuits obviously will pull a whole lot more amperage. I definitely will be exceeding the 5%. What should I do here? Redesign and get a different transformer?
I need some help here...
Thanks in advance!
I have installed a 45 kVA 480V 3ph / 240V 3ph w/120V CT. This particular transformer was installed, not for the need of 240V 3ph, but for 120V 1ph. The reason I went with a 3ph transformer was to keep an equal load on all 3 legs of our 3ph 4 wire system (I was told to do this by my boss at that time). Needless to say I now have a new boss that trusts my knowledge in installing what is appropriate. However, I have come to a point where I am needing to install another transformer that is identical to the first one I explained (I already have it on location).
So, here's my questions...
In reading the specs for this 45 kVA transformer, it gives these... "Installation Notes. CAUTION: When using the 120V center tap for single-phase applacations, the single-phase load should not exceed 5% of the three-phase kVA rating. Connect the X3 "high leg" tot he "B" phase per NEC 384-3 (do not use X3 leg for 120V lighting)."
This has caused 3 questions for me.
1. I did not know this, and I've already installed 1 of these solely for the 240/120 1ph. I connected all 3 legs on the primary side and only X1, X2, and X4(center tap). X3 was left unterminated. This particular transformer is supplying 4 - 20A 120V circuits, each of which rarely(if at all) will pull 20A and a drill press which operates on 240V at approx. 9.5A. So, am I OK in this setup? Hopefully so, because to explain that I need to change all that equipment out will go over like a lead balloon.
2. I have an indentical transformer as the one described above (just got it delivered yesterday). My plan was to wire it the same way. It will be supplying 6 - 120V 20A circuits, again each of which will never pull the full 20A. I'd be surprised if this system pulls 20A total across all circuits combined. Am I OK to continue with this plan? OR should I redesign and start over? I think I'll be OK, but would like to know what you more experienced folks think.
3. I will be installing another system like the ones described above, only a tad bit bigger. The plan was to use a 75 kVA transformer (same configuration as previous transformers). However, this system was to supply 3 welders and a plasma cutter (4 - 50A circuits), and several 120V circuits for grinders and sanders. These circuits obviously will pull a whole lot more amperage. I definitely will be exceeding the 5%. What should I do here? Redesign and get a different transformer?
I need some help here...
Thanks in advance!