Re: 3 prongs configured with ground in 2 wire system?
My dryer and range are wired in a VERY similar fashion.
My dryer and range are wired in a VERY similar fashion.
No need, on my part. I agree with you. I think my explanation says the same thing. I intentionally chose my wording in a way that would put at least a small amount of fear in the mind of a DIY who wants to connect N-G in a receptacle. In fact, the DIY was my intended audience for that particular explanation.Originally posted by rattus:. . . I maintain that there is little danger unless the neutral is open or highly resistive. Normally there would be at most a volt or so on the neutral--not enough to notice. . . Will provide sketches if you wish.
Golfrick1: Can you address this for us? In whatever training you had to undergo to get your job as a Home Inspector, what were you taught with regard to opening electrical equipment?</font>Originally posted by jimwalker:But one thing we might bring up is that it is questionable if a HI is allowed to pull a receptacle out to inspect.
I have been railed by this situation, on 120 v and 277 v systems.Originally posted by rattus:
and I maintain that there is little danger unless the neutral is open or highly resistive. Normally there would be at most a volt or so on the neutral--not enough to notice.
even with the neutral in tact,.. I HAVE BEEN RAILED BY THIS PERSONALLY. There is no IF in my opinion. THIS IS A HAZZARD!!!!!!!!Originally posted by rattus:
jb, I don't think anyone is calling this a minor problem. I am simply saying that as long as the neutral presents a low-R path to ground, there is little danger.
But, if the neutral opens, then we have a real danger--more dangerous than an open EGC would be. And, we all know that neutrals become open from time to time. As I have already said, "An accident waiting to happen".
Could you explain please, up until very recently every electric dryer and range was grounded in this way and I have not heard of a trail of victims from this practice.Originally posted by jbwhite:
]even with the neutral in tact,.. I HAVE BEEN RAILED BY THIS PERSONALLY. There is no IF in my opinion. THIS IS A HAZZARD!!!!!!!!
if you read the thread the short was intentionaly placed between the neutral and ground at the rec. to fool a inspectors tester.Originally posted by rattus:
JB,
I cannot see how a neutral or EGC in good condition could energize a piece of conduit.
Sounds like there was a short from line to conduit--quite possible. Or is it possible that your ladder was somehow energized like the baptismal pool with the faulty heater?