kwired
Electron manager
- Location
- NE Nebraska
- Occupation
- EC
They are still conductors in parallel to one another, they just have more then minimum conductor size that is in violation with 310.10(H).But they are NOT electrically joined at both ends. One conductor starts at the source and the other starts at a switch. That would make them "miss the boat" in two ways.
1.) not electrically joined
2.) not the same length
At least figure 6 is that way. Can't see all of figure 5, it just shows it going back towards the panel.
Also, IMO, electrically joined would mean constantly joined. With a switch they are not joined at all times. Maybe the section could be written more clearly but I think we all know what the intent was for parallel circuits.
We have debated the parallel conductor thing here many times for certain situations usually involving control schemes, not necessarily control wiring, but any power control scheme that has an "or" function in it's design may cause questions with parallel conductors here.
I think NEC needs to clarify whether they intend 310.10(H) to apply to any possible parallel conductor situation or just for when conductors are joined together to effectively make a higher current carrying capacity conductor out of them. Don't tell me to submit a "public input" formerly known as a change proposal, because I don't know what they intend this to apply to in the first place. That needs to be known before one can actually make a valid proposal IMO. I guess maybe you sent two public input proposals one for each side of the fence and hope they consider whichever one applies and reject the other?