Log # 1648
2- 168 - (210-70(c)-(New): Accept in Principle SUBMITTER: Ralph R. Bickner, Kimball, SD
RECOMMENDATION: Add paragraph (c) to 210-70 (c) Where lighting outlets are installed according to (a) above in stairways, there shall be a wall switch at each floor level to control the lighting outlet when the difference between floor levels is three steps or more. All switches installed according to (a) and (b) in 210-70 shall be installed on the strike side of the door when installed next to a doorway in which a door is installed.
SUBSTANTIATION: At the present time the NEC requires wall switches but does not specify where they are to be located. This can create some real hazards. When inspecting residences, the biggest complaint homeowners have is "why don't you require a three-way switch for stairways so I don't have to go back down to the landing to shut off the entrance stairway light once I have reached the living area". This creates a safety hazard as they are subject to using the stairway without lighting. In both residential and commercial installations, switches for many rooms, especially rest rooms are found behind the door so that it is necessary to go into a dark room and nearly close the door to get to the switch. This may be called a design problem but it is also a safety problem when you have to stumble around in a dark room to find the switch.
PANEL ACTION: Accept in Principle. The Panel accepts (c) but change "three steps" to "six steps". The Panel rejects the second paragraph.
PANEL COMMENT: Six steps is the reasonable difference in floor levels. In some cases it is impractical to locate the switch as requested.
VOTE ON PANEL ACTION; Unanimously Affirmative.