- Chapel Hill, NC
- Retired Electrical Contractor
Here is an article by Stallcup that I scanned from a magazine that pertains to the OP's question.
We solved a similar problem with a small two car unattached garage by removing the panel in the garage, replacing it with an A/C disconnect that includes a gfci receptacle. We now have a single 20 amp branch circuit feeding a garage. Neutrals & EGs are isolated. All items are gfci protected. No GES required. Plus wehave the disconnecting means. Works if customer does not need or require more than one BC.
I probably would have made it a 120V panel before doing that.
Interesting point-- my bet is that the way the NEC is written your install is non compliant. I wrote a proposal to change this. The NEC allows a sp switch but the disconnect would have to be service rated. Most a/c discos are not service rated. 225.36
BTW, I have never seen anyone get turned down for it.
The NEC also allows a set of 3 way switches to be the disconnect. A non service rated switch of either single throw or pull out style is usually at least indicating of whether it is on or off. Could this exception use better wording --yes.
If you have an inspector that doesn't allow the AC disconnect --- you have an inspector that thinks he is a god and what he thinks is the way it is. (I toned it down quite a bit from what my first thoughts were)
I agree and this exception is only for residential. So if that is the case then it seems as if a mwbc cannot be used for a non residence unless there are non fused disconnects that are service rated. I believe that Chris (Raider) made a proposal to get that changed.
For garages and outbuildings on residential property, a snap switch or a set of 3-way or 4-way snap switches shall be permitted as the disconnecting means
I am not following. I was saying that snap switches or a/c discos cannot be used for non residential separate structure disconnects unless the a/c disco is service rated. IMO, this would make using a MWBC or single branch circuits non compliant in non residential settings.
The amount of breakers for disconnect of the structure is 6.
225.33 Maximum Number of Disconnects.
(A) General. The disconnecting means for each supply
permitted by 225.30 shall consist of not more than six
switches or six circuit breakers mounted in a single enclosure,
in a group of separate enclosures, or in or on a switchboard.
There shall be no more than six disconnects per
supply grouped in any one location.
"Suitable for use as service disconnect"
Again.........is the detached garage power considered a "service"?
ARTICLE 225
Outside Branch Circuits and Feeders
II. Buildings or Other Structures Supplied by a
Feeder(s) or Branch Circuit(s)
225.36 Suitable for Service Equipment. The disconnecting
means specified in 225.31 shall be suitable for use as
service equipment.
Exception: For garages and outbuildings on residential
switches shall be permitted as the disconnecting means.
Article 100, definition of "Feeder"
Read the definitions of feeder and branch circuit.
If you have breakers in the garage, you have a feeder, not a branch circuit.
No, not if it is supplied from another buildings service.
But it does not matterbecause in most cases 225.36 requires a service rated disconnecting means for the feeder to a detached building.
Besides a label inside, what makes a disconnect "suitable as service equipment"?
Or what determines the rating as "service rated"?
24. A panelboard intended for service equipment use must have the marking “Service Disconnects” near the switch or circuit breaker handles. If this is not done in the factory, pressure sensitive labels must be provided. This marking identifies the service disconnects when branch disconnects are
also present. This is required by Section 230.70(B) of the NEC.