brielellalyse
Member
can you put 3 wires under a staple? i use 9/16 size staples or that doesn't matter. i live in southern,nj.
334.30 Securing and Supporting.
Nonmetallic-sheathed cable shall be supported and secured by staples, cable ties, straps, hangers, or similar fittings designed and installed so as not to damage the cable, at intervals not exceeding 1.4 m (4? ft) and within 300 mm (12 in.) of every outlet box, junction box, cabinet, or fitting. Flat cables shall not be stapled on edge.
Sections of cable protected from physical damage by raceway shall not be required to be secured within the raceway.
Are you trying to open the 110.3(B) worm can?:roll:Dennis Alwon said:I don't see where it matters.
I could use a nail bent over the wires as long as it is protected from damaging the cable
chris kennedy said:Are you trying to open the 110.3(B) worm can?:roll:
Let me say I agree but it could be argued:Dennis Alwon said:I don't see where a staple needs to be listed anyway. If it secures the cable to the wall so be it. As long as you aren't bundling. You can use cable ties or whatever you want IMO
(B) Installation and Use. Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling.
If a staple is used I would follow the manufactures instructions.Equipment. A general term, including material, fittings, devices, appliances, luminaires, apparatus, machinery, and the like used as a part of, or in connection with, an electrical installation.
Dennis Alwon said:And if a nail is used what instruction would you follow then. Hypothetically, of course, because you nor I would do this.
buckofdurham said:What type of nail. Some nails have been treated with chemicals that could corrode the insulation on the wire.
You have to use the right type of nail in treated wood for example. They now use nails other then galvanized for treated wood.
buckofdurham said:Them Durham guys don't miss very much.
Kenan over in Hillsborough use to look at every staple.
I think he has moved to Alamance now.
buckofdurham said:Really
Oh and congratulations, I heard you we're elected president of the orange county EA.