That's not going to happenI'm have been intrigued by OP and the string of posts. If I were the OP I would apologize to the inspector as it being an oversight, that you are completely aware of the color white represents and it is a rudimentary practice to re-identify it.
True, but for 15 and 20 amp circuits. This is a 30 amp circuit and # 10 wire.I'm sure it would be agreed that the color white is commonly recognized as a grounded conductor and as it has been applied per the OP it certainly isn't grounded
A serious code violation ?? Are you for real ? First of all, anyone removing a panel cover or a disconnect cover while it is energized better know what they are doing. If you're working live on the water heater end and don't realize it's a 240v unit you're in a lot more trouble than you think. And, if you're working in a breaker panel and see a # 10 white wire terminated on a 2-P, 30 amp breaker do you take it off the breaker and move it over to the ground bar just because it's a white wire ?and poses to be a serious code violation and safety hazard. Getting zapped by a conductor that one understands to be grounded may not be a good thing.
Look, I've already admitted I was wrong by not re-identifying the white wire but you have to think about the logic in this situation. Who am I marking the white wire for ? The homeowner ? If it's another EC isn't he going to realize that the # 10 white wire on the 2-p, 30 amp breaker is an ungrounded conductor ?