I recently had someone tell me that they've been told that it's an NEC requirement to keep the conductors of a multi-conductor cable (like MC) twisted together within a panel because of 300.20. Please stop the insanity. BTW I hate the wording of this section.
hmy:
Has anyone else heard of people enforcing this?
Has anyone else heard of people enforcing this?
300.20 Induced Currents in Ferrous Metal Enclosures
or Ferrous Metal Raceways.
(A) Conductors Grouped Together. Where conductors
carrying alternating current are installed in ferrous metal
enclosures or ferrous metal raceways, they shall be ar-
ranged so as to avoid heating the surrounding ferrous metal
by induction. To accomplish this, all phase conductors and,
where used, the grounded conductor and all equipment
grounding conductors shall be grouped together.
Exception No. 1: Equipment grounding conductors for
certain existing installations shall be permitted to be in-
stalled separate from their associated circuit conductors
where run in accordance with the provisions of 250.130(C).
Exception No. 2: A single conductor shall be permitted to
be installed in a ferromagnetic enclosure and used for skin-
effect heating in accordance with the provisions of 426.42
and 427.47.