300.3(b)??
M. D.
Got a question for you,.. The other day I had to re-wire a 4 zone tankless boiler , one circulatro fed from the aquastat on the boiler the others from a taco control relay. I fed the taco control and then because this control was remote from the boiler , I ran the circulator (3 switched) wires over to a j-box on the boiler where I picked up the neutral for the circs. It is the same neautral just in a different spot the circs are only an amp each so there should be no problem there ... 300.3 may be ? you can see the control here page 90 tankless app.on the right.
I would say its a violation of 2008 NEC 300.3(B). it says ...'where used, the grounded conductor and all egc and bonding shall be within the same raceway...'
M. D.
Yeah 'where used' Hmmm .. I kinda view the relays as a switch I don't always run the neautral to my switch ...
Dennis Alwon
Chapel Hill, NC
Electrical Contractor
MD, I am not sure I follow you-- if you say have a feed from the same circuit in two 3 way switch location and the hot goes up to the light from one switch while the neutral goes to the light from the other three way location then this is a violation unless it is in NM cable. You will get emf's from this setup.
