And I always looked at the small plate for bored holes through members. They put that little protector plate on the stud face. But the wire was not protected to the left or right of the stud. The requirement is also an 1 1/4" back from that face of stud or protected ? I always looked at that and wondered if that would need protection and per the code it does, but never really addressed, or nothing made for that location. Handbooks and depictions show one thing and the verbiage states it's required. That plate was removed many times, by the sheet rock crew and planers. You could see the locations it was removed from on Insulation inspection. Once removed they never put back on. It just gets a little frustrating sometimes when you actually look at the codes and requirement's and always hoped for some kind of clarification or it was addressed better. As an inspector, I tried to learn as much as possible, and make the right calls, but the code gets confusing sometimes. What's very confusing for me, is that you have these code requirements for protection locations and exceptions listed. You have a plastic box within 1/2" of stud face, (backside of interior wall), and sometimes closer with a deeper junction box. The plastic box is not a ' listed exception' and this distance is not the required 1 1/4' needed from framing member face...Now what ? I have always looked at that and wondered if I am missing it. It would be great if this was addressed more. How can this not be explained or addressed better in the code ?? Am I missing something ?